Have a site lighting drawing that say 20A circuits shall not exceed 1500VA and 15A circuits shall not exceed 1150VA. How do I make sure I don't put too many light poles on one circuit? Do I kneed to look at the fixture watts? Thanks.
GoldDigger
Placerville, CA, USA
Retired PV System Designer
Yes, you need to start with the fixture watts, and know what bulb and driver will be fitted if there are options.
Then you look at the power factor (PF) of the fixture and divide the watts by the power factor to get the VA.
kwired
Electron manager
NE Nebraska
Must be 120 volt circuits in your application, 1500 VA on a 277 volt circuit is only about 5.4 amps, advantages of using 277 over 120 kind of go away if you are still limited to 1500 VA.
infinity
New Jersey
Journeyman Electrician
Wouldn't the ballast or driver have all of that figured out and just give you the amount of current it draws?