How do the volt sticks, such as a Fluke AC1 work? The instructions state that "If no indication, voltage may still be present".
Does it work with capactance to ground thru the body???
 
Tom
They do work through capacitive coupling. As has been stated, these are good as indicators only and a tester is the final test, especially since your life may depend on it.

I will say that the manufacturers have improved on these devices considerably in the last few years.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I always test mine first by shaking it next to my rubber coated gloves. It will light up and beep.
 

RayS

Senior Member
Location
Cincinnati
infinity said:
I always test mine first by shaking it next to my rubber coated gloves. It will light up and beep.

Yep. My Gardner-Bender will give me a quick confidence beep when I turn it on, the Fluke doesn't. Both respond to the "static" test.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
There is a new and improved version of the Fluke volt stick. It beeps to let you its working.
Also the new Fluke 117 meter has a built in inductive voltage alert, and a special "Low Z" that allows it to be used where there are ghost voltages. The DVM have a high input impedance and don't load a circuit like the old analogs.
Cost of the 117 is about $170. Heres the link
http://us.fluke.com/usen/products/Fluke+117.htm?catalog_name=FlukeUnitedStates
 

edamico11

Senior Member
Location
NJ
To be honest...

To be honest...

I do not trust the beep and the light on mine. I first plug it into a circuit known to be live and make sure it functions properly. Just anile I guess..
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Even when you have tested the the non-contact tester before and after testing the unknown wire, it can still tell you that there is no power when there really is. This can happen when testing NM or SO where the paper or fiber under the jacket is wet. This can give a false negative. A false positive is not a safety hazard, but a false negative is.
Don
 

mdshunk

Senior Member
Location
Right here.
I have often gotten false negatives on the very thick type TW insulation. If I can, I try to check where the conductor might be skinned out.
 