Re: Voltag Drop
No, what I am trying to state is that sizing the conductor for the continuous load is required, the volatge drop calculation is not. So, you first need to determine what size conductor is required for the circuit. Once you determine that, you can check to see if other circuit conditions present a voltage drop issue.
So again using the example of a 45-ampere continuous load, the "I" would be 45-ampere, but the "cm" would be based on 56.25-ampere rated conductor.
Am I making more sense?