Voltage at disconnect higher that at breaker.

Status
Not open for further replies.

TME

New member
Location
Boston
Commercial strip
120/208 3phase
Tanning Bed

the bed calls for 1 phase 208

208v at breaker.
230v at line side of pullout disconnect with bed disconnected.

feeder is about 40’ long run above the drop ceiling.
any thoughts.???
i have yet to look in the ceiling.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As Digger suggested a transformer somewhere. The few beds that I've hooked up all needed 240 volts not 208.
 