I'm feeling like a chump.
Troubleshooting a bathroom light that has a dim glow when the switch is off. I disconnected the switch and am getting 6V AC on my digital multimeter (so not a bad switch). Homeowner mentioned another light had the same issue so they used a halogen to make the glow disappear. I found 6V AC there as well. I'm getting 124V at circuit breaker (to neutral bar). GEC to water at house intake is present, but I haven't confirmed rods.
"All" knob and tube was supposedly replaced by romex a while back, but the wiring I see looks like homeowner work everywhere (neutrals landed on ground bar, loose wires all over attic).
I have a sneaking suspicion that this particular circuit still has some knob and tube as the J-box in the attic that ties the power to the switch leg for the fixture had all the grounds loose - that is, not tied together (something I might do if replacing a section of knob and tube with romex and protecting with a gfci somewhere upstream). Still can't see how that would be related to 6v between disconnected switch leg and ground. I know a floating neutral gives me 30-80V AC on my ddm sometimes, so I'm thinking this is current on neutral somehow and a "floating" switch leg (when the switch is off). Again, feeling like a chump and really hoping someone can help.
Troubleshooting a bathroom light that has a dim glow when the switch is off. I disconnected the switch and am getting 6V AC on my digital multimeter (so not a bad switch). Homeowner mentioned another light had the same issue so they used a halogen to make the glow disappear. I found 6V AC there as well. I'm getting 124V at circuit breaker (to neutral bar). GEC to water at house intake is present, but I haven't confirmed rods.
"All" knob and tube was supposedly replaced by romex a while back, but the wiring I see looks like homeowner work everywhere (neutrals landed on ground bar, loose wires all over attic).
I have a sneaking suspicion that this particular circuit still has some knob and tube as the J-box in the attic that ties the power to the switch leg for the fixture had all the grounds loose - that is, not tied together (something I might do if replacing a section of knob and tube with romex and protecting with a gfci somewhere upstream). Still can't see how that would be related to 6v between disconnected switch leg and ground. I know a floating neutral gives me 30-80V AC on my ddm sometimes, so I'm thinking this is current on neutral somehow and a "floating" switch leg (when the switch is off). Again, feeling like a chump and really hoping someone can help.