looking for ideas. went to a call, owner saying that they are getting a shock when they touch a hose bibb. stuck a probe in the ground and attached a meter lead to it and the other to the bibb 14 volts present. went though the usual test turning off breakers and watching meter. turn off all single pole breakers and no change start turning off two pole breakers, turn off pool pump and voltage drops to 9 volts, turn off water heater and drops to 5 volts, turn off a/c and drops to 2 volts, with all breakers off still has 2 volts. water lines are all copper, bonded to to the ground rod conductor. panel is bonded, all connections tight. this is a home built in the 70's three wire entrance from meter to panel. about 25'. called Power co. they came out changed some ground rods a transformer, underground service from trans to meter about 30'. does no mater which two pole breaker is no or combination of two pole breakers the voltage goes up and down about 4 volts each accordingly. also measured at the ground rod with probe in the ground about 2 feet from ground rod one meter lead on probe the other on ground rod conductor 5-6 volts. measured from hose bibb to ground rod conductor 0 volts. any help will be welcome. Thanks