Primary source is assumed to be a stiff one. Loss of that source will certainly load up the backup source resulting to large current draw, hence a larger voltage drop in the system will occur. There is a point where the system voltage can drop below the level where the field forcing cannot maintain the voltage anymore, core saturation, allowed period of field forcing limits, tap changer's lower/upper limits, etc.
You don't question why such things happen in the system under consideration. It is a product of voltage collapse studies simulated in advance to give the designer points to consider when trying to coordinate settings.