hamburgerpatty
My application is a continuous lighting load of 78 amps at 240volt single phase.
My distance is 475' away from source.
My question is "Do I take in account my continuous load first before I calculate for voltage drop, or what?"
I come up with;
78 * 1.25 = 97.5 Amps for continuous
97.5 A *2*K*475/cm = 3/0 wire = 6.1 volt = 2.6% Vdrop
If I don't have to wory about the continuous load in my calcuation for voltage drop requirements.
I come up with
78 A *2*K*475/cm = 2/0 wire = 6.2 volt = 2.6% Vdrop
and the 2/0 wire would meet my requirements for continuous load @ 125% of FLA
What is the correct procedure for calcuating Voltage Drop while taking in a continuous load that is 475 feet away from the source?
I come up with;
I come up with