We are installing #10 THHN for 20amp/277V lighting circuits because of the distance - (voltage drop)
We have 10 current caring conductors that we want to put in a single conduit, the derating of a #10 THHN is 20amps at 50% per table 310.15(B)(2)(a).
Is ther any other issues I'm missing because of the voltage drop and derating of the same condutors?
Thanks, Mark
We have 10 current caring conductors that we want to put in a single conduit, the derating of a #10 THHN is 20amps at 50% per table 310.15(B)(2)(a).
Is ther any other issues I'm missing because of the voltage drop and derating of the same condutors?