Is it neccesary to increase the ground size when voltage drop requires circuit wires to be increased? If so how do you size the equipment ground for a 20 amp circuit that has been sized at #6 thhn for V.D.?
Actually, that's an easy one to figure out. For a 20 amp circuit, the ungrounded conductors and the equipment grounding conductor are the same size (i.e., #12). When you increase the size of the ungrounded conductors, all you have to do to "increase the EGC proportionally" is to, once again, match the size of the EGC to the size of the ungrounded conductors. In your example, you need the EGC to be size 6.sevlander said:. . . how do you size the equipment ground for a 20 amp circuit that has been sized at #6 thhn for V.D.?