So he is the situation: I have 45KVA XFMR, the primary current is 54A x 1.25 = 68A -> 70A CB, the wire size is #4 AWG.
Now, what if the 45KVA XFMR is 450 ft away from its over current protection, the #4 AWG is no longer good due to the voltage drop, now I'd have to go with #2 AWG.
Now my question is, for such a long run do I still size my CB to be 70A or it should be sized based on that #2 AWG?
Now, what if the 45KVA XFMR is 450 ft away from its over current protection, the #4 AWG is no longer good due to the voltage drop, now I'd have to go with #2 AWG.
Now my question is, for such a long run do I still size my CB to be 70A or it should be sized based on that #2 AWG?