- Occupation
- Junior plan reviewer
I have situation in which plans call for 480V to 120/208V three phase 75 kva transformer with taps. The transformer secondary feed 120/208V panelboard A. The panelboard A has two branch circuits b1 and b2 . B1 feeds site lights 600 feet away and b2 feeds site lights 400 feet away all with 120V single phase.
Also panelboard A serves small garage loads such as receptacles, heaters.
The branch circuit conductors size for b1 and b2 is #8. I asked for voltage drop calculation and was told that the 75kVA has taps can compensate for voltage drop to branch circuit and their is no need for up sizing the cables.
I always thought it is better to do voltage drop even with taps.
Questions:
1. Can branch circuits 600 feet away be compensated with taps adjustment to not to have voltage drop and cable size remain same?
2. Is their an exception to not having voltage drop from taps in code?
3. Can 250.122(B) apply if voltage is increase due to tap but not cable size?
Also panelboard A serves small garage loads such as receptacles, heaters.
The branch circuit conductors size for b1 and b2 is #8. I asked for voltage drop calculation and was told that the 75kVA has taps can compensate for voltage drop to branch circuit and their is no need for up sizing the cables.
I always thought it is better to do voltage drop even with taps.
Questions:
1. Can branch circuits 600 feet away be compensated with taps adjustment to not to have voltage drop and cable size remain same?
2. Is their an exception to not having voltage drop from taps in code?
3. Can 250.122(B) apply if voltage is increase due to tap but not cable size?