Hope you're all having a great morning,
I was looking at Mike Holts voltage drop equations page and have a couple questions (This page).
For VD formula he uses:
[FONT="]"VD = 2 x K x Q x I x D/CM - Single Phase[/FONT]
[FONT="]VD = 1.732 x K x Q x I x D/CM - Three Phase[/FONT]
[FONT="]“VD” = Volts Dropped: The voltage drop of the circuit conductors as expressed in volts.[/FONT]
[FONT="]“K” = Direct Current Constant: This is a constant that represents the direct current resistance for a one thousand circular mils conductor that is one thousand feet long, at an operating temperature of 75º C. The direct current constant value to be used for copper is 12.9 ohms and 21.2 ohms is used for aluminum conductors. The “K” constant is suitable for alternating current circuits, where the conductors do not exceed No. 1/0.[/FONT]
[FONT="]“Q” = Alternating Current Adjustment Factor: Alternating current circuits No. 2/0 and larger must be adjusted for the effects of self-induction (skin effect). The "Q" adjustment factor is determined by dividing alternating current resistance as listed in NEC Chapter 9, Table 9, by the direct current resistance as listed in Chapter 9, Table 8.[/FONT]
[FONT="]“I” = Amperes: The load in amperes at 100 percent, not 125 percent for motors or continuous loads.[/FONT]
[FONT="]“D” = Distance: The distance the load is located from the power supply, not the total length of the circuit conductors.[/FONT]
[FONT="]“CM” = Circular-Mils: The circular mils of the circuit conductor as listed in Chapter 9, Table 8."
My questions are:
When my conductor is 2/0 or larger, do I use BOTH K and Q? Then just use K for <2/0 conductor?
For I (load current), could I just use the rating of the OCPD to get a worst case scenario?
For distance, just curious why conductor length isn't used? Because it is harder to measure with loops in boxes, and distance between panels is close enough?
Thanks for your guys time, I'm new here and will probably have a lot more stupid questions for you![/FONT]
[FONT="]
[/FONT]
I was looking at Mike Holts voltage drop equations page and have a couple questions (This page).
For VD formula he uses:
[FONT="]"VD = 2 x K x Q x I x D/CM - Single Phase[/FONT]
[FONT="]VD = 1.732 x K x Q x I x D/CM - Three Phase[/FONT]
[FONT="]“VD” = Volts Dropped: The voltage drop of the circuit conductors as expressed in volts.[/FONT]
[FONT="]“K” = Direct Current Constant: This is a constant that represents the direct current resistance for a one thousand circular mils conductor that is one thousand feet long, at an operating temperature of 75º C. The direct current constant value to be used for copper is 12.9 ohms and 21.2 ohms is used for aluminum conductors. The “K” constant is suitable for alternating current circuits, where the conductors do not exceed No. 1/0.[/FONT]
[FONT="]“Q” = Alternating Current Adjustment Factor: Alternating current circuits No. 2/0 and larger must be adjusted for the effects of self-induction (skin effect). The "Q" adjustment factor is determined by dividing alternating current resistance as listed in NEC Chapter 9, Table 9, by the direct current resistance as listed in Chapter 9, Table 8.[/FONT]
[FONT="]“I” = Amperes: The load in amperes at 100 percent, not 125 percent for motors or continuous loads.[/FONT]
[FONT="]“D” = Distance: The distance the load is located from the power supply, not the total length of the circuit conductors.[/FONT]
[FONT="]“CM” = Circular-Mils: The circular mils of the circuit conductor as listed in Chapter 9, Table 8."
My questions are:
When my conductor is 2/0 or larger, do I use BOTH K and Q? Then just use K for <2/0 conductor?
For I (load current), could I just use the rating of the OCPD to get a worst case scenario?
For distance, just curious why conductor length isn't used? Because it is harder to measure with loops in boxes, and distance between panels is close enough?
Thanks for your guys time, I'm new here and will probably have a lot more stupid questions for you![/FONT]