Is the distance always doubled, or is the length only taken once? I've seen examples of both.
Allow me to interpret or rather put in other terms for others.Actually, for a balanced three phase load the voltage drop, based on the current in a phase conductor not the nominal line to line load current, is just based on the and one run of wire.
Is the distance always doubled, or is the length only taken once? I've seen examples of both.
What really bugs me is that online VD calculators "automatically put in 1X, 2X, or even 1.732X based on your choice of DC, 120/240, or three phase, but do not tell you what they are doing. And different ones make different choices!
If using the line-to-neutral voltage, one should either use 2xD or just 1xD and figure the neutral separately.
True, in the sense that when you have a balanced-linear-load MWBC, there is 0 current on the neutral and the load end of the neural is also at 0 volts relative to source end neutral.There is zero current on the neutral conductor for balanced linear three-phase loads.
When using line-to-neutral voltage, you use 1xD when calculating the effective length of the circuit.
What really bugs me is that online VD calculators "automatically put in 1X, 2X, or even 1.732X based on your choice of DC, 120/240, or three phase, but do not tell you what they are doing. And different ones make different choices!
Shouldn't be too hard to make your own in a spreadsheet. Can even easily put it online, such as a Google sheet on Google Drive or an Excel file on OneDrive.What bothers me, is that the online calculators lock you in to a common voltage selection with the drop-down menus. Sometimes I might want a custom DC voltage to be 421V. Or I might want European AC voltage to be 230/400.
Shouldn't be too hard to make your own in a spreadsheet. Can even easily put it online, such as a Google sheet on Google Drive or an Excel file on OneDrive.
I'll agree with Tony S. The BS7671 has been in some
ways more useful than the NEC tables for certian calculations
and design decisions over the past few years for me anyway.
Yes it takes on more of a guidance role for acceptability than
the NEC's more prescriptive approach. But it (BS7671) helped
with some abstract thinking that after working to NEC specs.
And now NESC regs. It is good to merge the thoughts together,
After all the electrons obey the same Physics regardless of the
governing athourity.
And I mean no disrespect to the views stated above.
JR
Can you provide an example, where BS7671 would be more useful than the NEC?