S stew Senior Member Location federal way,washington Nov 30, 2010 #1 a pole lite with a 22.5 amp draw located 325 ft from service. # 8 ok for that ? 240 v single phase Last edited: Nov 30, 2010
raider1 Senior Member Staff member Location Logan, Utah Nov 30, 2010 #2 If you want to maintain a 3% voltage drop then you would need to go with a #6. Using a #8 you would have a 4.8% voltage drop. Click HERE for a free on-line voltage drop calculator. Chris
If you want to maintain a 3% voltage drop then you would need to go with a #6. Using a #8 you would have a 4.8% voltage drop. Click HERE for a free on-line voltage drop calculator. Chris
S stew Senior Member Location federal way,washington Nov 30, 2010 #3 thanks. using a votage drop of 5% seems we are ok