Originally posted by dsewing: I get two very different numbers via these two formulas. Which is correct?
Is the one from the spreadsheet exactly, or very close to, double the other?
I tried to use the spreadsheet last night for my own purposes, and I suspected it had an error. Having read this thread this morning, I am certain the spreadsheet has an error. The error is not in the math or in the formulas, but rather in the instructions. Here is what I mean.
Originally posted by dsewing: The spread sheet posted on Mike's web site uses the following formula: 2k x length x current/circular mils.
I agree that this is the formula that the spreadsheet uses. I also agree that that is the correct formula. But I submit that the ?length? in that formula should represent the ?one-way distance.? You account for the fact that there are two conductors (i.e., the hot conductor going to the load and the neutral returning from the load) by use of the factor ?2? in the formula. But the instructions tell you to use, as the length of the run, ?Two times length of conductor in feet (length of 2 conductors).? To me, this looks like you are doubling the double. In other words, you should either enter the one-way distance into the formula, or if you use the two-way distance, you should drop the factor of 2.
May I ask the forum members for a comment?