Hi,
I was wondering if somebody could follow my voltage drop calculation to see if I am correct? See below:
Total amperage: 421A
Copper (K): 12.9
L = 700ft (one way)
CMA = 503,400 (3 sets of 3/0 copper = 167,800 x 3)
3 phase 480V circuit
1 pf
(1.732x12.9x421x700) ÷ 503,400 = VD
(6,584,423.16) ÷ 503,400 = VD
13.1 Volts
13.1V ÷ 480V = 2.7% VD
3 sets of 3/0 thwn copper OKAY
Thank you in advance