Voltage drop will be directly related to how much current is flowing. How much current is flowing is not related to what the setting of the overcurrent device is. It will effect how long until the overcurrent device opens if it is over the setting.
When doing voltage drop calcs do you use the calculated load in your figures or the size of the overcurrent protection?
For worst case use the max allowable loading on the breaker, i.e. 80% of the fixed trip setting for non 100% rated breaker.
You can draw 100% of the rating of the breaker as long as it is not continuous, three hours or more.
What's the consensus on considering power factor when calculating voltage drop? I have a 700+ ft. run from a generator with a PF of 0.8. This dramatically increases the 200A, 208V, 3-phase voltage drop calculation.
How much does the power factor change as a result of voltage drop over the length of wire? That is, for the sake of comparison, what is the difference in circuit power factor between 10' vs. 700'...?KW is not equal to KVA (except for purely resistive load), so you have to use KVA (which means pf).
How much does the power factor change as a result of voltage drop over the length of wire? That is, for the sake of comparison, what is the difference in circuit power factor between 10' vs. 700'...?
How much does the power factor change as a result of voltage drop over the length of wire? That is, for the sake of comparison, what is the difference in circuit power factor between 10' vs. 700'...?
What's the consensus on considering power factor when calculating voltage drop? I have a 700+ ft. run from a generator with a PF of 0.8. This dramatically increases the 200A, 208V, 3-phase voltage drop calculation.
KW is not equal to KVA (except for purely resistive load), so you have to use KVA (which means pf).
It's not a matter of the PF changing with distance. The source is a generator which the mfg tells us has a PF of 0.8. Therefore if I know my load of 200A, 208v, 3-phase I can calculate voltage drop at 700+ ft. I was taking into account the source PF as my load PF is negligible. Perhaps I'm looking at this wrong?
I'll advise you not to hold your breath while waiting... :huh:I'll wait for you to come up with a formula that figures that one out, and how it affects voltage drop!!
I'll advise you not to hold your breath while waiting... :huh:
Not totally true. See NEC chapter 9, table 9. The wiring method affects reactance and thus impedance. The table even shows impedance for a power factor of 85%....
If you know the max current, the power factor has no bearing on the voltage drop.
I'll advise you not to hold your breath while waiting... :huh:
For worst case use the max allowable loading on the breaker, i.e. 80% of the fixed trip setting for non 100% rated breaker.