Joe perkins
New member
When figuring voltage drop calculations for the test do you use the voltage that is actually stated or do you use nominal voltages
Joe perkins said:When figuring voltage drop calculations for the test do you use the voltage that is actually stated or do you use nominal voltages
weressl said:At point of delivery - main panel, switchgear - you would use the nominal system voltage and allow -2% maximum. At the distribution level delivery point you would use the allowed voltage drop allowed at that point - that would be 2% - and use the maximum -3% for the voltage to be delivered to the user terminals.
roger said:These numbers, (2% & 3 %) are not requirements only suggestions.
Roger
weressl said:These numbers are ANSI/IEEE requirements that are designed to allow the manufacturers uniformly design equipment that will operate within the expected voltage variations and allow the desing engineers to appropriately design the sytem with the load flow studies.
roger said:That's fine and dandy but, most (I would say all) electrical exams don't give a hoot about a manufactures design criteria.
Another point is that most electrical exams are dealing with theory and NEC requirements, not ANSI/IEEE requirements.
Roger
weressl said:Oh really? I did not know that NEC was elevated to the rank of an engineering Standard.
Once again, that's fine and dandy but, I doubt any Journeyman exam takes this into a very deep consideration or even cares.weressl said:The design criteria is imposed upon the manufacturer by the existence of the ANSI Standard, they may add even narrower design criteria with additional NEMA standards so the USER can expect uniform performance.
I think I was the one who pointed that out earlier.weressl said:NEC did and does not establish voltage drop allowance levels.
And I think most do.weressl said:It would behoove any electrical educator to explain to the electricians how the whole system works, how utilities generate power, what regulations guide them, what happens when it is distributed - yet another entity -, the local independent distributors, the users, the engineering firms role to assure the quality of power delivered, how OSHA, NFPA fits in and so on.
I pretty much agree with this.weressl said:When one clearly understands his or her role in the system as a whole, could perform their work with more responsibility, and understand where their role starts and stops and who is responsible for what.
Uh, what, I don't understand. :grin: (sorry, cuoldn't help myself)weressl said:The questions and comments on this site testify that there is a mass confusion in this area and that results in a lot of misunderstanding and misconception.
weressl said:(as he gingerly steps off the soapbox as the audience errupts in..
a hearthy laughter......
weressl said:The design criteria is imposed upon the manufacturer by the existence of the ANSI Standard, they may add even narrower design criteria with additional NEMA standards so the USER can expect uniform performance.
weressl said:Oh really? I did not know that NEC was elevated to the rank of an engineering Standard.
roger said:These numbers, (2% & 3 %) are not requirements only suggestions.
I would think in an exam the question would be more on the line of "what is the VD of a circuit..." or "What is miniumum size conductor for a VD of _____ in a feeder 1500 feet in length...
Roger
weressl said:The numbers ARE requirements, not suggestions.
FPN No. 2: Conductors for feeders as defined in Article 100, sized to prevent a voltage drop exceeding 3 percent at the farthest outlet of power, heating, and lighting loads, or combinations of such loads, and where the maximum total voltage drop on both feeders and branch circuits to the farthest outlet does not exceed 5 percent, will provide reasonable efficiency of operation.
(C) Explanatory Material Explanatory material, such as references to other standards, references to related sections of this Code, or information related to a Code rule, is included in this Code in the form of fine print notes (FPNs). Fine print notes are informational only and are not enforceable as requirements of this Code.
roger said:Sorry Laszlo, you are wrong.
Remember, this is a code forum and the NEC is the code most talked about here (not saying discussions outside of code do not have a place here, they certainly do) and as far as the NEC is concerned 2% and 3% VD numbers are not part of the NEC, they are only suggestions/recommendations that show up in a FPN, for example. 215.2(A)(3)
Now for clarification of what part a FPN plays in the NEC
Roger
Don410.300(a) Standard voltage. Each entity supplying electrical energy for general use shall adopt a standard service voltage of 120 volts (when measured phase to neutral) and shall maintain the service voltage within the allowable variations from that value at all times.
(b) Allowable voltage variations. For service rendered at the standard service voltage, voltage variations as measured at any customer's point of delivery shall not exceed a maximum of 127 volts nor fall below a minimum of 113 volts for periods longer than two minutes in each instance. For service rendered at voltages other than the standard voltage value, voltage variations as measured at any customer's point of delivery shall not exceed 10% above or below the service voltage for a longer period than two minutes in each instance.