VD = sqrt(3)*L*R*I , 3 phase
-------------
1000
VD = 2*L*R*I , 1 phase
-------------
1000
high leg delta system.
chiller MCA: 214 A, 3 phase
heater current: 10 A, 1 phase, A phase
A = 214 + 10 = 224 A
B = 214 = 214 A
C = 214 = 214 A
Neutral = 10 A
Is this the correct way to add currents per phase?
An engineer I asked said that you would just add the 3 phase and single phase loads directly.
Would it be ok for me to use the 3 phase voltage drop formula using single and 3 phase loads?
-------------