Voltage Drop Calculations w/ single and three phase loads

Status
Not open for further replies.

Murloc

Member
Location
Louisiana
Occupation
Engineer Intern 1
VD = sqrt(3)*L*R*I , 3 phase
-------------
1000

VD = 2*L*R*I , 1 phase
-------------
1000
high leg delta system.
chiller MCA: 214 A, 3 phase
heater current: 10 A, 1 phase, A phase

A = 214 + 10 = 224 A
B = 214 = 214 A
C = 214 = 214 A
Neutral = 10 A

Is this the correct way to add currents per phase?
An engineer I asked said that you would just add the 3 phase and single phase loads directly.

Would it be ok for me to use the 3 phase voltage drop formula using single and 3 phase loads?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Under the approximation that the load current doesn't change with voltage drop, then the superposition principle would apply for calculating voltage drops. That's because V = I Z is a linear relationship between V and Z when I is fixed.

So you can separately calculate the 3-phase voltage drop for the 3-phase equipment using the 3-phase formula, and the single-phase voltage drop for the single-phase equipment using the single-phase formula, and add them up for the case that both loads are operating simultaneously. Note that when you add the voltage drops for the two loads, it will be a vector addition. As the 3-phase drop will move each of A, B, and C voltage towards their centroid, while the single phase voltage drop would move A and N towards their midpoint.

Cheers, Wayne
 

Murloc

Member
Location
Louisiana
Occupation
Engineer Intern 1
Under the approximation that the load current doesn't change with voltage drop, then the superposition principle would apply for calculating voltage drops. That's because V = I Z is a linear relationship between V and Z when I is fixed.

So you can separately calculate the 3-phase voltage drop for the 3-phase equipment using the 3-phase formula, and the single-phase voltage drop for the single-phase equipment using the single-phase formula, and add them up for the case that both loads are operating simultaneously. Note that when you add the voltage drops for the two loads, it will be a vector addition. As the 3-phase drop will move each of A, B, and C voltage towards their centroid, while the single phase voltage drop would move A and N towards their midpoint.

Cheers, Wayne
right so you're saying that if you get

2% VD 120V single phase, A
2% VD 240V three phase, A

you add them together
4% VD @ 120V, single phase
4% VD @ 240V, three phase
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Not quite. That would work if your single phase load were connected line to line, say A-B. Then the A-B VD would be 4%, with the A-C and B-C VDs being less.

If you have a 240V high leg delta, and you calculate the 3-phase VD for a balanced 3-phase load per the formula in the OP, that's the L-L VD. So if it's 2%, L-L decreases from 240V to 235.2V. The voltages A-B, B-C, and C-D are still equal to each other.

If you have a 2-wire A-N load on that system, and calculate its VD with the single phase formula, that's the VD A-N. The voltages of B and C don't change. And the A-N VD occurs half as voltage rise on N and half as voltage drop on A. So if it's 2%, then the A-N-B voltages would go from 120 / 0 / -120 to 118.8 / 1.2 / -120 from that load alone.

If you have both VDs at once, then the L-L voltages will no longer be balanced. You can say that the B-C VD is 2%, the A-B VD is 3% (not 4%, as half of the A-N VD occurs on N, half on A), and the A-C VD is somewhere between 2% and 3%, the exact value of which would require some vector calculation.

If you only care about the worst case L-L VD, then it would 3%.

Cheers, Wayne
 
Last edited:

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
P.S. There's a nice vector diagram that goes along with this question/answer, so if that's not clear to you, let me know and I'll figure out how to do a vector drawing and post it as an image.

Cheers, Wayne
 