The inspector should be able to cite the reference document and paragraph that requires you to demonstrate compliance.
Where is the project located? Check your state's building code energy conservation section as suggested by Ron. Voltage drop considerations are due to increased energy consumption (I
2R heat loss) that increased amperage resulting from fixed loads operating a lower voltages will cause. The building codes could care less if the equipment works or not. There is an exception for feeder and branch circuits dedicated to emergency circuits.
We have had permitting reviews that request clarification on voltage drops before, but they don't actually check the calculations. We actually put a value on the drawings for significant loads. That being said, they are looking at it, depending on which municipality you are working with. The lazy way to do it is to put a note saying voltage drops have been considered according to the standard. Many AHJ's will consider this adequate since they can point to it if there is indeed an issue and the EE will end up taking responsibility for the oversight if they didn't actually do the calculation
For reference:
Florida Building Code, 5th Edition (2014), Energy Conservation
C405.7.3 Voltage drop.
C405.7.3.1 - Feeders and customer owned service conductors.
Feeder and customer owned service conductors shall be sized for a maximum voltage drop of 2 percent at design load.
C405.7.3.2 Branch circuits.
Branch circuit conductors shall be sized for a maximum voltage drop of 3 percent at design load.
Here is a official FBC response to a question regarding voltage drop.
TLDR;
Question:Can EE's design construction projects to allow feeders more than 2% VD as long as feeder + branch VD does not exceed 5%?
Answer: No.