Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
I don’t understand entirely why, when I solve algebraic for unknown CM size (NEC chapter 9 table 8) of conductor able to yield less than 3 percent voltage drop from source to final breaker, I get a CM/ AWG size too small for the ampacity required
For a 3 phase Delta delta, 4800 volt primary 480 volt secondary, secondary current 360.85 amperes I get an answer of 1/0 aluminum wire good for only 120 amperes with a voltage drop of 14.4 volts
14.4 volts/ 480 volt is within target 3% voltage drop but the answer yields a conductor less than allowed for its ampacity
Is this to say this is the minimum size wire to yield this VD?
14.4 VD = 1.732 (3 phase) x 21.2 (copper K resistance per foot mill) x 360.08 (Amperes) / divided by unknown CM
SOLVE FOR CM
For a 3 phase Delta delta, 4800 volt primary 480 volt secondary, secondary current 360.85 amperes I get an answer of 1/0 aluminum wire good for only 120 amperes with a voltage drop of 14.4 volts
14.4 volts/ 480 volt is within target 3% voltage drop but the answer yields a conductor less than allowed for its ampacity
Is this to say this is the minimum size wire to yield this VD?
14.4 VD = 1.732 (3 phase) x 21.2 (copper K resistance per foot mill) x 360.08 (Amperes) / divided by unknown CM
SOLVE FOR CM