Voltage Drop & Feeder Sizing

Status
Not open for further replies.

chicagosparky

Member
Location
Chicago, IL
Need some input here, have to install a 200 Amp, single phase service for a remote cell tower with a 400 ft underground feed in PVC to the utility transformer. When I read Sec 215.2 Informational Note No. 2 is states we are to design the feeder to a maximum of a 3% voltage drop which results in 500 MC copper conductors. It also goes on to say a 5% VD to the farthest outlet. If I plug in 5 %, I can use 4/0 copper conductors. Per Code, am I allowed to use the 4/0 conductors?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Informational notes are not enforceable; they are not "code." So to disregard them is not a "code violation." The real question is whether the equipment at the far end of the line will operate properly at a lower voltage.
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Need some input here, have to install a 200 Amp, single phase service for a remote cell tower with a 400 ft underground feed in PVC to the utility transformer. When I read Sec 215.2 Informational Note No. 2 is states we are to design the feeder to a maximum of a 3% voltage drop which results in 500 MC copper conductors. It also goes on to say a 5% VD to the farthest outlet. If I plug in 5 %, I can use 4/0 copper conductors. Per Code, am I allowed to use the 4/0 conductors?

Voltage Drop is based upon the amps of the load. The equipment might be rated higher.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would use the 60 amps for the VD calculation and size according to that as long as the conductors are still good for at least 200 amps.
 

Kansas Mountain

Senior Member
Location
Oklahoma, United States
Occupation
Lighting and Lighting Control Designs
No idea how cell towers actually work, but with 5G expecting to roll out over the next several years, is it possible your client wants the voltage drop calc'd assuming max load on the conductors so there isn't an issue adding more equipment to towers in the near future?
 

xptpcrewx

Power System Engineer
Location
Las Vegas, Nevada, USA
Occupation
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Just a quick comment: Be careful with oversimplified voltage drop calculations only factoring resistances and not the reactance component as they will give false results.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
We wired power and ground for a cell site on top of a 10-story apartment building. The copper wire sizes were spec'ed, as was the RGS conduit, so there was no debate as to size.

We only had use of an elevator twice taking stuff up, and once coming down. The rest of the time, we had to take stairs . . . from the basement. My knees were quite angry at me.
 