Hello! Wanted to see everyone opinion on this.... voltage drop usually makes very paranoid for bigger type buildings. I'm getting a total of less than 5%VD all the way from the utility transformer secondary location for the building to the farthest branch circuit.
Utility transformer to main building metering service (200FT) = 2.08%VD
Building metering service to each condo electrical panel (130FT (Farthest point)) = 2.14%VD
Condo electrical panel to farthest branch circuit 'condenser roof top-unit' = .75%VD
Total = 4.97%VD (this is assuming the building load is at 100% load demand)
I usually like to stay with 3%VD, i worry about the motor operated type equipment like the condenser since it says 230/208V and my service is 208V/120. I understand that motors can usually go as low as -10%VD. Do you think 5% or less VD is sufficient or should i be even more careful and try to make it less than that? Again keep in mind that this is peak 100% load demand.
Thank you,
Thank you,