Voltage drop for G-GC Cable

Status
Not open for further replies.

rockman33

Member
Location
Alabama
I completely understand to apply the voltage drop formula to a single say THHN conductor but, is there anything different when doing this for a 4 - wire G-GC type cable?
 

Smart $

Esteemed Member
Location
Ohio
Typical voltage drop calculations do not make any adjustment for insulating materials, proximity to other conductors, surrounding medium, ambient temperature, etc. Most are based solely on conductor element (Cu or Al), cross-sectional area (wire size), and distance.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
If the manufacturer does not indicate the cable impedance then you may calculate it following-for instance:
Electric Power Research Institute EPRI
Power Plant Electrical Reference Series Volume 4 Wire and Cable
EL-5036 V4 Project 2334
ch.4-4 CABLE SIZING -VOLTAGE DROP
Or see:
http://okonite.com/engineering/EHB 2010.pdf
Engineering Handbook Section 3 Voltage Regulation [pg.12]
 