NEC recommends 5% voltage drop for branch circuits and feeders but what about service conductors? Potentially running 2,000 feet of service conductor length.
NEC recommends no more than 3% on either feeder or branch, and not more than 5% total. Service conductors are not covered in this recommendation. If it were my design to defend, I would blend it in with the constraint on voltage drop for the feeders, such that feeders + service conductors do not exceed 3%.
Since the ONE in this case would be POCO, it is very unlikely to happen unless the customer is very persuasive.I see a lot of 4/0 URD aluminum used for 240v 200 amp 1ph services coming from the utility pole to the line side of the meter on the house, mostly out of habit.
I would think when the utility pole is located 100 ft or so from the house, then another 35 or 40' up the pole to reach the Transformer one should probably start considering upsizing the wire for voltage drop although I hardly ever see that happen.
JAP>
I believe most POCO adhere to the ANSI C84.1 standard at the point of use (i.e. the service disconnecting means?; example)....
Conductors upstream of the service point are under the exclusive control of POCO, and might have a 5% drop all on their own and still allow POCO to meet their voltage delivery commitments...
Since the ONE in this case would be POCO, it is very unlikely to happen unless the customer is very persuasive.
That varies from POCO to POCO.No.
The customer provides the wire from the pot on the pole to the line side of the meter base.
JAP>
No.
The customer provides the wire from the pot on the pole to the line side of the meter base.
Unless the house has a lot of electric heat a 200A service is already upsized and would not need larger wire.I see a lot of 4/0 URD aluminum used for 240v 200 amp 1ph services coming from the utility pole to the line side of the meter on the house, mostly out of habit.
I would think when the utility pole is located 100 ft or so from the house, then another 35 or 40' up the pole to reach the Transformer one should probably start considering upsizing the wire for voltage drop although I hardly ever see that happen.
JAP>
Unless the house has a lot of electric heat a 200A service is already upsized and would not need larger wire.
Not here.
That's the way it is here: 10 feet of conduit on the pole and enough wire to get to the pot. Utility puts u-guard the rest of the way. So in your area for underground, utility aways provides wire to meter? I assume you have to provide conduit then per their specs?
That's the way it is here: 10 feet of conduit on the pole and enough wire to get to the pot. Utility puts u-guard the rest of the way. So in your area for underground, utility aways provides wire to meter? I assume you have to provide conduit then per their specs?
When I see 'from pot to the line side of the meter base' I assume overhead lines.
Apparently jap was specifically talking underground while the OP did not specify.
People in more populated areas probably think of "underground" as being a situation where the utility conductors are also underground and the connection is in a vault.
Service Conductors, Overhead. The overhead conductors
between the service point and the first point of connection
to the service-entrance conductors at the building or other
structure.
Service Conductors, Underground. The underground
conductors between the service point and the first point of
connection to the service-entrance conductors in a terminal
box, meter, or other enclosure, inside or outside the building
wall.
everyone uses "underground" to refer to a service that is overhead lines, down a pole, underground to meter and service equipment
In that case though you are not doing the overhead at all are you? The overhead would be the utility and 98% of your work is the underground portion save for a riser at the pole and meter right?
Let's just say they are both. :happyyes:... Or we could just say there are neither overhead nor underground service conductors?