Voltage Drop for Switchgear Controls

Status
Not open for further replies.

faresos

Senior Member
Hello everyone:

I'm working on a project that will require to provide external 48VDC for switchgear controls. The battery bank is about 200ft away and the load is about 43Amps at 48VDC. Based on 3% we will need #3/0 cables which I'm concern about if I can terminate this size in terminal lugs. My question is: What is the maximum voltage drop allowed for the DC system that will make the system operational?

Thanks,
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
My experience it is only with Power Stations. In my opinion, at first you have to double-check the list of DC consumers[including possible reserve for future extension] and to split the list in two parts:
one where all receivers are in operation all the time and the second for instruments acting for short time.
A 5% voltage drop-from rated-will be o.k. for continuous operation and 10% for sudden increased load.
ANSI T1 315 states that equipment shall operate properly for its intended service life with voltage variations between -42.0 Vdc and -56.7 Vdc measured at the first distribution point of the equipment. 42 V it will be 12.5% voltage drop.
IEC 60255 states the voltage limits 37.5 to 60 V for 48 V rated.
 