I tuypically use teh folowing VD formula for three phase feeders:
cm = kx1.72xIxD/vd
where,
cm = circular mils of conductor
k= resitvity of copper (12.9)
I = current
D = distance (one way)
VD = allowable voltage drop
for long runs with multile sets this formaul does not seems to work. For example, a 2000a feeder, 200 ft long, 480v with desired VD of 2%.
plugging in the values,
cm = 12.9 x 1.72 x 2000a X 200ft/9.6v = 929,875 cm
diving by 500,000cm i get 1.8 sets of 500kcm condcutors. Not right.
Anyone know what I'm doing wrong.