The complete voltage drop formula is as below
VD = (1.732*I(RcosO + XSino)*l*100/(1000*380)......(i)
in this formula
R = Resistance ohm/km/per
X = Reactance ohm/km/per
O(Tetha) = ArcCosin(p.f)
I=Ampere
l=length
380 = line to line Voltage and we know that
220 line to neutral = 380/1.732 (line to line voltage) it is substitude because of impedances are per phase so we must use line to neutral voltage (220) or 380/1.732 volt.
The above information is a real formula for voltage drop calculation.
But if you want to make your work easy or do it fast we can substitude the following as below
From cable catalog we take Resistance per km and Reactance per km
and make a factor
factor(k) = 1.732*(RcosO + XSinO) we make this factor for each cable size.
In formula (i) there length and current are two variable which varies every time. but factor(k) remains constant for a specific cable size.
So, formula number (i) changes as below for a specific cable size
VD = k*I*L*100/(1000*380)
So, in your formula the factor 2.K.I.D = CM
can be a constant
If it is DC wire then reactance is zero and the power factor will be one and there will be only resistance
Hope it is done.