What is the voltage drop on a 1/0- 3 conductor type G cable on a 600' feeder @ 240 volt, single phase with a 200 amp load?
Actually it is rated for 207 amps in a single phase case.AFIK, 1/0 type G is not rated for 200 amps. Is this a test question / homework?
Roger
Column "E" is used in a single phase case like this. Which is rated at 207 amps.Rated at 181 in the 75°C column if Table 400.5(A)(2), so cannot be used for a 200 amp load.
There is also an issue with using any of the cables in that table at the table ampacities because 110.14 says we can only use the Table 310.15(B)(16) ampacities. That table is 310.16 in the 2020 code.
Current ratings are based on the ability of the insulation to withstand heat. (That's why we do VD calcs based on the resistance/size, not the insulation type.)G cable has substantially higher current ratings than THHN or other normal wire.
The engineer on the job states that because of that the G cable also has a higher amp rating, it is also more tolerant regarding VD.
I did skip over the use of column E. However, I still see no permission in the code that permits you to uses that cable at that ampacity when directly connected to any type of equipment.Column "E" is used in a single phase case like this. Which is rated at 207 amps.
The 200 amp load in the example is an example of an actual connected load.Next question: how to get the engineer to reconsider this point without making it a fight.
I agree with the above comments; no permission in the code to use this cable at this amp rating, and voltage drop will be no better than THHN of the same gauge and length.
One possible voltage drop calc issue: you say '200A', however is the load really 200A, or is it a circuit protected by a 200A breaker? They are two different things. If you have a circuit protected by a 200A breaker, the actual load might be less than 200A...or if the load has significant starting current then you might see even more than 200A for short periods of time. You need to use the actual current flow to calculate voltage drop.
-Jon
The 200 amp load in the example is an example of an actual connected load.
In this particular case the load is power pedestals on floating docks at a marina.
Two pedestals with (2) 50 amp, 240 volt receptacles each.
Regarding the insulation reply above, I expressed that exact argument to the engineer.
I told him that I have always understood current ratings of conductors to be directly related to the insulation type.
So I agree still with that.
His response was regarding the fact that G cable is highly stranded.
That current travels on the surface of the conductors and that is why the G cable is so capable of both higher current ratings and better VD tolerances.
He went on to say that he has proven it thru testing.
His response was regarding the fact that G cable is highly stranded.
That current travels on the surface of the conductors and that is why the G cable is so capable of both higher current ratings and better VD tolerances.
Amazed anyone found this table 400.5(A)(2), with cables operating at such high temperatures.Rated at 181 in the 75°C column if Table 400.5(A)(2), so cannot be used for a 200 amp load. (or if only 2ccc, 207A in column E)
There is also an issue with using any of the cables in that table at the table ampacities because 110.14 says we can only use the Table 310.15(B)(16) ampacities. That table is 310.16 in the 2020 code.
Have him install it.Next question: how to get the engineer to reconsider this point without making it a fight.
-Jon
It's late chiming in but maybe the engineer looked at the instructions at the foot of the table 400.59A2)! Since the type-G cable was 3-conductor, the correct rating of the conductor is 181A (column F, 75 deg), not 207A as pointed out!Amazed anyone found this table 400.5(A)(2), with cables operating at such high temperatures.
Don points out 110.14(C)(1) instruction shows 200A on 1/0cu may be ~113°C, which far exceeds 75°C equip. maximums.
Per Chap.9, Tbl 8, Note 2, 200A operates on 1/0cu @ 113°C.
Per Chap.9, Tbl 9, Note 2, 600ft of this @ 240 volts drops to 207 volts, and 120v drops to 87v.
Switch mode power supply nameplates, Computers, TV's, etc, show a 100vac minimum.
A vault transition to 10ft of 3/0cu pigtails at equip. termination may bring 195A down to 75°C, but voltage drop remains problematic ~14%.