Anybody can help me selecting molded case circuit braker and conductor size for transformer and main panelboard .

there is a transformer primary 120/208
secondary 220/380V,30KVA.
cable connecteed primary length 135m.
cable connected secondary is 5m.
What would be cable size and molded case circuit braker will be in feeder panelboard.
Thanks.
 

templdl

Senior Member
Location
Wisconsin
Re: Voltage Drop help?

Your transformer rating doesn't make sense. From what I guess the transformer probably is 3ph with a 208y/120 primary and a 380y/220 secondary making it a wye-wye which would be very unusual for a small 30kva transformer.
If it were a single phase is the primary 208v which can be reconfigured to be applied at 120v? And the secondary, is it 380v with a tap at 220v?
 

bennie

Esteemed Member
Re: Voltage Drop help?

The transformer makes sense in the US. I don't think it is needed in Europe.

Multiply 1.094 times 135 metres to find yards. Multiply yards times 3 to find feet.

Your numbers are 443 feet, and 16.41 feet. respectfully.

The primary at full load is 83 amps.

The rest of the math is yours :eek:
 