I am wondering what is the voltage drop limits per ANSI/IEEE and NEC for MV branch circuit and feeder.
I got a 23kV pri to 2484V sec transformer, connected to a VFD connected to an induction motor (radial system). My induction motor is 2.3kV rated. I see a voltage drop of 7.15% at the motor bus which makes my end voltage to 2306V which is acceptable for the motor
But, is that much voltage drop allowed per ANSI/IEEE? I know for LV system the limit is 5% (feeder 2% and branch 3%). Does the same apply for MV?
Thanks in advance for your advise
I got a 23kV pri to 2484V sec transformer, connected to a VFD connected to an induction motor (radial system). My induction motor is 2.3kV rated. I see a voltage drop of 7.15% at the motor bus which makes my end voltage to 2306V which is acceptable for the motor
But, is that much voltage drop allowed per ANSI/IEEE? I know for LV system the limit is 5% (feeder 2% and branch 3%). Does the same apply for MV?