I have a voltage drop issue on a 115v single phase minus 70 freezer. The freezer draws 24 Amps when the compressor starts. We had past issues with the breaker tripping and increased the wire size to #10 Thhn on a 30 amp breaker. This seemed to solve the nuisance tripping for a while. We are now experiencing problems again. There are no joints in this run and the home run is approximately 160 feet from panel to source. When the compressor starts we have 115V at the breaker but only 89V at the unit with a 24 amp draw. I preformed a voltage drop calc and the calcs told me the max drop should be a little under 10V. Does anyone have any suggestions on why i would only have 89V at the unit when the compressor kicks in?
Also, my service Tech tells me the compressor is fine in this unit.
Also, my service Tech tells me the compressor is fine in this unit.