Hi All,
I am rather new to the Electrical field, but man do I love it. I had a hopefully quick theory/calculations question regarding voltage drop.
If I have a 9 amp lighting circuit and the furthest light from the panel is 350ft, can I still use a #12?
My answers
1. No you cannot run a #12 because NEC 210.19 (A) Max 3% VD - Correct? [I calculated a VD of around 12.5% (VD=2*I*R*L/1000) = 2*9*1.98*350/1000 = 12.5%]
2. (My theory question) if you did run a #12 would this just mean the current would basically increase by 12.5% and now be 10.125A? So the lighting would still work, it would just be less efficient? I get what voltage drop can do to motors, I guess in my head I don't find it to be a big deal when I think about lighting.
Honestly this is just a check on my theory of circuits. Hope I wasn't too confusing.
I am rather new to the Electrical field, but man do I love it. I had a hopefully quick theory/calculations question regarding voltage drop.
If I have a 9 amp lighting circuit and the furthest light from the panel is 350ft, can I still use a #12?
My answers
1. No you cannot run a #12 because NEC 210.19 (A) Max 3% VD - Correct? [I calculated a VD of around 12.5% (VD=2*I*R*L/1000) = 2*9*1.98*350/1000 = 12.5%]
2. (My theory question) if you did run a #12 would this just mean the current would basically increase by 12.5% and now be 10.125A? So the lighting would still work, it would just be less efficient? I get what voltage drop can do to motors, I guess in my head I don't find it to be a big deal when I think about lighting.
Honestly this is just a check on my theory of circuits. Hope I wasn't too confusing.