rpg
Member
- Location
- Kailua, HI, USA
Our electricians calculated the conductor size of a single instrument circuit (industrial plant) @ 120 vac, 1210' in length, with a 20 amp breaker (per schedule) to require #3/0 conductor. The designers responded that the actual load of the instrument is 24W and that a #12 conductor is sufficient. NEC 210.18 seems to indicate that conductors should be sized on the overcurrent device installed on the circuit. Could someone please provide more insight on this?