Hi All,
I'm turning to this forum hoping to get some opinions and hopefully learn something new.
I have a power system study I'm currently working on that involves determing the % voltage drop when starting the largest motor (125HP) in the system. I have done some in the past with no issues but this one has some weired results I'm hoping someone here might have an answer to or share their experience with a similar issue.
A brief summary of the system is as follows:
-There are two power sources via an ATS - 1 utility and 1 gen, the gen is a 320kW and the utility source is via a 750kVA XFMR and both are supplying the system @480V. The largest loads are 3 motors (a 125HP and 2 60HP) in the system fed from VFDs without by-pass contactors.:happyno:
In the past studies I've done, there were no VFDs involved just regular DOL starters and in one case a RVSS which I had to do a transient motor analysis rather than a static one.
Procedure/Issue:
The procedure to run the LF with motor starting is to first run the analysis with all motors running (depending on the system and specs) to determine the %VD at the gen or utuility bus and then adjust it to be close to the rated voltage as possible with the assumption that the utility is supplying power at rated voltage at the service entrance point (XFMR primary is my preference) or in the case of the gen that it has a perfect exciter and voltage regulator to maintain the volatge at 480V. In this case, the sofware (PTW) has options to adjust the "Initial Operating Conditions" to achieve this. However, when the initial conditions are adjusted such that the %VD at the gen bus/terminal is 0%VD, the motor switched to "starting", and analysis rerun the new %VD at majority of the busses are negative implying that the motor is generating some extra power and returning it back into the system. This is opposite to what one should expect. I can only attribute this to the VFD the motor is connected to since VFDs do not present the inrush issues associated with DOLS, RVSS, and Soft Starters but I'm not sure how the software handles this. I read a little bit on VFDs with Regen capabilities which the software also considers or at least gives you the option to select but this doesn't seem to change the results regardles of the option chosen. Another thing I noticed is that the software has an option to adjust the "Initial Operating Conditions" specific to the VFD on the VFD page options. However, when this is adjusted based on the calculattion ; pu=Bus voltage/480V (not sure if this is the right way) there's no signifiact improvement.
I'm relative new to this and not too familiar with VFDs but I'm also willing to learn. I'll appreciate all comments/suggestions I can get.
Thanks.
I'm turning to this forum hoping to get some opinions and hopefully learn something new.
I have a power system study I'm currently working on that involves determing the % voltage drop when starting the largest motor (125HP) in the system. I have done some in the past with no issues but this one has some weired results I'm hoping someone here might have an answer to or share their experience with a similar issue.
A brief summary of the system is as follows:
-There are two power sources via an ATS - 1 utility and 1 gen, the gen is a 320kW and the utility source is via a 750kVA XFMR and both are supplying the system @480V. The largest loads are 3 motors (a 125HP and 2 60HP) in the system fed from VFDs without by-pass contactors.:happyno:
In the past studies I've done, there were no VFDs involved just regular DOL starters and in one case a RVSS which I had to do a transient motor analysis rather than a static one.
Procedure/Issue:
The procedure to run the LF with motor starting is to first run the analysis with all motors running (depending on the system and specs) to determine the %VD at the gen or utuility bus and then adjust it to be close to the rated voltage as possible with the assumption that the utility is supplying power at rated voltage at the service entrance point (XFMR primary is my preference) or in the case of the gen that it has a perfect exciter and voltage regulator to maintain the volatge at 480V. In this case, the sofware (PTW) has options to adjust the "Initial Operating Conditions" to achieve this. However, when the initial conditions are adjusted such that the %VD at the gen bus/terminal is 0%VD, the motor switched to "starting", and analysis rerun the new %VD at majority of the busses are negative implying that the motor is generating some extra power and returning it back into the system. This is opposite to what one should expect. I can only attribute this to the VFD the motor is connected to since VFDs do not present the inrush issues associated with DOLS, RVSS, and Soft Starters but I'm not sure how the software handles this. I read a little bit on VFDs with Regen capabilities which the software also considers or at least gives you the option to select but this doesn't seem to change the results regardles of the option chosen. Another thing I noticed is that the software has an option to adjust the "Initial Operating Conditions" specific to the VFD on the VFD page options. However, when this is adjusted based on the calculattion ; pu=Bus voltage/480V (not sure if this is the right way) there's no signifiact improvement.
I'm relative new to this and not too familiar with VFDs but I'm also willing to learn. I'll appreciate all comments/suggestions I can get.