I am starting a job where someone else has abruptly left off.

A 480-Volt Sub-Panel supplies power to two Refrigeration Units. That Sub-Panel is located 1560 feet from the Main Panel and is supplied by 4/0 Aluminum Feeders. According to the calculation Vd = (√3(21.2) x L x I)/CM, the maximum current carrying capacity of these Feeders is 53 ampere if no more than a 3 percent voltage drop is allowed. The Feeders are presently protected with a 125-Ampere OCPD located at the Main Panel.

Should the 125-Ampere OCPD be replaced with a 60-Ampere OCPD because that is the maximum current (53 Amperes rounded up to the next ?Standard Size?) that the Feeders can carry and remain within 3 percent voltage recommended by the NEC?
 
I am starting a job where someone else has abruptly left off.

A 480-Volt Sub-Panel supplies power to two Refrigeration Units. That Sub-Panel is located 1560 feet from the Main Panel and is supplied by 4/0 Aluminum Feeders. According to the calculation Vd = (√3(21.2) x L x I)/CM, the maximum current carrying capacity of these Feeders is 53 ampere if no more than a 3 percent voltage drop is allowed. The Feeders are presently protected with a 125-Ampere OCPD located at the Main Panel.

Should the 125-Ampere OCPD be replaced with a 60-Ampere OCPD because that is the maximum current (53 Amperes rounded up to the next “Standard Size”) that the Feeders can carry and remain within 3 percent voltage recommended by the NEC?
It's not required. Additionally, refrigeration units may need the higher COPD to avoid nuisance tripping on startup.
 
Should the 125-Ampere OCPD be replaced with a 60-Ampere OCPD because that is the maximum current (53 Amperes rounded up to the next ?Standard Size?) that the Feeders can carry and remain within 3 percent voltage recommended by the NEC?

Current is a function of the load, not the 'circuit' OCPD.

If you want to maintain the 3% voltage drop, you either increase your conductor size or decrease the load.
All the NEC cares, is that the OCPD protects the conductor.
 
... All the NEC cares, is that the OCPD protects the conductor.
Motor conductors are a bit different than most other load types. For the most part, they don't have an OCPD per se. They have a Ground Fault, Short Circuit protective device [fuse(s) or breaker], while the conductors are protected from overcurrent by the motor overload protection scheme.
 