I am starting a job where someone else has abruptly left off.
A 480-Volt Sub-Panel supplies power to two Refrigeration Units. That Sub-Panel is located 1560 feet from the Main Panel and is supplied by 4/0 Aluminum Feeders. According to the calculation Vd = (√3(21.2) x L x I)/CM, the maximum current carrying capacity of these Feeders is 53 ampere if no more than a 3 percent voltage drop is allowed. The Feeders are presently protected with a 125-Ampere OCPD located at the Main Panel.
Should the 125-Ampere OCPD be replaced with a 60-Ampere OCPD because that is the maximum current (53 Amperes rounded up to the next ?Standard Size?) that the Feeders can carry and remain within 3 percent voltage recommended by the NEC?
A 480-Volt Sub-Panel supplies power to two Refrigeration Units. That Sub-Panel is located 1560 feet from the Main Panel and is supplied by 4/0 Aluminum Feeders. According to the calculation Vd = (√3(21.2) x L x I)/CM, the maximum current carrying capacity of these Feeders is 53 ampere if no more than a 3 percent voltage drop is allowed. The Feeders are presently protected with a 125-Ampere OCPD located at the Main Panel.