I got involved in an interesting question question on another website [Taunton/Breaktime]. This question involves a string of five outdoor lights, each being 1 amp apiece. The arrangement is as follows:
"Fuse" 60' 1st light 175' 2nd light 175' 3rd light 190' 4th light 220' 5th light. He is using the voltage drop calculator on Electrician's Toolbox.com [3% vd] and needs to know the wire size.
I pointed out that the wire size could diminish as the amp loads got further out. But using the calculator, I ended up with some wierd results: Namely, #14 for the first 60' to feed 5 amps, #10 Al between light 1 and 2, #12 to carry 3 amps between light 2 and 3, #12 3 to 4; and #14 for the last run.
But just inputing 1 amp for the last fixture at 820', I got #10 guage Aluminum.
Oh yeah!: 120 volts.
Would appreciate some wisdom.
~Peter
"Fuse" 60' 1st light 175' 2nd light 175' 3rd light 190' 4th light 220' 5th light. He is using the voltage drop calculator on Electrician's Toolbox.com [3% vd] and needs to know the wire size
I pointed out that the wire size could diminish as the amp loads got further out. But using the calculator, I ended up with some wierd results: Namely, #14 for the first 60' to feed 5 amps, #10 Al between light 1 and 2, #12 to carry 3 amps between light 2 and 3, #12 3 to 4; and #14 for the last run.
But just inputing 1 amp for the last fixture at 820', I got #10 guage Aluminum.
Oh yeah!: 120 volts.
Would appreciate some wisdom.
~Peter