Voltage drop with air compressor
Voltage drop with air compressor
A little about the building being served. It is part of a complex of commercial units occupied by product manufactures, retail/wholesale sales supplies etc.
Each unit has from one to five 120/208V 200A elec panels, the feeders are 3/0 copper.
The unit I'm referring to is less than 100 ft away from the switchgear (PG&E Main) and is supplied by a 200A 3 phase "Y" CB. Didn't think that a voltage drop on the lines could be a problem, because the voltage is within NEC specs, but I could be wrong.
I also didn't think that three buck/boost transformers were the right solution for the compressor, hoping for a different approach to boost the voltage up just 8 or so volts.
The compressor sits about 30 ft away from the elec panel and is supplied by 3 #10 THHN conductors and one #10 grounding conductor in a fuseable disconnect, fused at 50A CL.
Compressor requirements are: 208V 28.8A and the control transformer is on the 208V tap, of the several taps that are available, inside the unit.
The measurements I took were from the: CB, the load side of the disconnect and the contractor block (inside the unit). everything had the same voltage (199-201 volts line to line, 118-121 volts line to ground) Amps were from about 21A to 27A running load. I had my (true RMS) meter on high/low record for a few minutes on each test.