Re: voltage drop on motors
When sizing wires for a motor application it is sometimes advantageous to oversize the wires beyond the minimum requirements as spelled out in the NEC - this is an engineering, not safety, issue. Sometimes voltage drop on start is very critical on devices with large inertia or high torque requirements - remember that torque is related to the square of the voltage - so a drop to 75% of rated voltage at the motor terminals will result in a drop to 56.25% of available torque. So, yes wires to motors may be oversized to reduce voltage drop - depending on the application - like say a NEMA C 60hp motor with across-the-line-start (or even SCR) on a belt conveyor. Or even one with a fixed fill fluid coupling if torque is close. On a DC motor app the speed is directly related to voltage applied - so if you do not have tach-feedback the motor will slow down on heavy loads due to voltage drop - this may or may not be a problem depending on app.