whbaxter912
Member
- Location
- Houston, Tx
- Occupation
- Electrician
We have a 600ft run of 3 parallel sets of 500kcmil AL. When we put a load bank at the far end we see 7v of vdrop on phase 3 ONLY plus ~30a of current on the neutral and ~30a of current on the ground with about 1v between neutral and ground. When we put the load bank at the service there is no vdrop(thinking impedence coming from xformer) but there is current on the neutral and ground. The measurements were taken with a Hioki PQA. We have toned out the neutral and ground looking for a floating neutral and there is none. We have meggered all the phase conductors. We have thermal imaged all the terminations and found nothing outstanding. We have not toned out the phase conductors as we assumed crossing one of the 3 conductors per phase would cause an immediate breaker trip. Thoughts as to why only L3 would have the vdrop and to why the current on the neutral and ground?