I have a 120v sewage pump that is located in an outside tank system. The system has 3 floats and a 1hp pump. The remote exterior control panel nameplate is telling me to figure the pump draw at 16 amp. I have 100' thru the house (extreme opposite corners) and another 30' from the control to the vault. VD calc tells me to use #10 cu. Would I be defeating the purpose of using the #10 thru the house if the last 30' from the control to the vault was #12? The excavator who installed the vault did me a huge favor and ran 3/4" PVC u/g for the raceway with what looks to be at least 3 90's. The float controls can be #14 but the #10's are whats killing me. Unable to re dig raceway because of concrete and pavers already in place.Spent an hour getting a tape thru .