Am I doing this voltage drop formula correctly?
I am running a feeder line to a detached garage which is about 85 feet from the load center. It is 120volt line, 20 amp, using the voltage drop formula I come up with running an No. 8 awg to maintain a 3% drop in voltage. Does anyone have any comments about using a No. 10 or even No. 12 for this circuit? It seems to me a No. 10 would be sufficient but according to this formula it is more than 3%.
8awg: 26.4 x 85ft x 20a / 16510mils = 2.72 volts
10awg: 26.4 x 85 x 20 / 10380mils = 4.32 volts
12awg: 26.4 x 85 x 20 / 6530mils = 6.87 volts
I am running a feeder line to a detached garage which is about 85 feet from the load center. It is 120volt line, 20 amp, using the voltage drop formula I come up with running an No. 8 awg to maintain a 3% drop in voltage. Does anyone have any comments about using a No. 10 or even No. 12 for this circuit? It seems to me a No. 10 would be sufficient but according to this formula it is more than 3%.