I'm working on a job where literally nothing is grounded and the wire length is around 2.5miles. I'm trying to calculate what size ground I would need to install to meet the NEC requirements in reference to voltage drop. Breaker size is 100A, actual load of about 15A and fed by 2 3/0cu conductors @ 480v. Also, in the same conduit is another 2 conductor 1/0cu circuit, 480v. I have been searching the code book and this forum and haven't been able to come out with an answer I feel totally comfortable with. I know table 250.122 tells me that the 100A circuit should be protected by a minimum wire size of #8awg. I also know that an increase in the ungrounded conductor size requires that the EGC also be increased in size "proportionally according to the circular mill area of the ungrounded conductors" (250.122(B)). I'm confused as to how exactly I'm supposed to calculate that.. Do I need to start with the cmil of a #3awg (310.16 for 100A) and subtract it from the area of a 3/0 and then apply that percentage to the ground?? Seems like I'm missing something. Any help would be appreciated!