Hi Gentlemen,
Here's the scenario: Barn is 350' from house... Customer said they just needed lights and plugs so I buried #2 URD between them. Now they are talking making an apartment in the barn, i.e. more load!
Am I wrong in thinking that I'm only gonna get 20 amps out there at best?
And just for fun, what are the risks of feeding this wire from a 100A breaker? My thought is that if they have a load that with voltage drop pulls 90 some amps but less than 100 amps, just for arguments sake, isn't there a fire hazard risk of burning up the wire before the breaker trips?
One last question since it's been a few years since I've had this class... when calculating this, I would use 120v because that's what I have per leg, correct? Yes, it's ultimately a 2P 240v circuit, but 120v per leg, so vd calc should use 120 here I believe??
Thank you guys. Stay safe.
Here's the scenario: Barn is 350' from house... Customer said they just needed lights and plugs so I buried #2 URD between them. Now they are talking making an apartment in the barn, i.e. more load!
Am I wrong in thinking that I'm only gonna get 20 amps out there at best?
And just for fun, what are the risks of feeding this wire from a 100A breaker? My thought is that if they have a load that with voltage drop pulls 90 some amps but less than 100 amps, just for arguments sake, isn't there a fire hazard risk of burning up the wire before the breaker trips?
One last question since it's been a few years since I've had this class... when calculating this, I would use 120v because that's what I have per leg, correct? Yes, it's ultimately a 2P 240v circuit, but 120v per leg, so vd calc should use 120 here I believe??
Thank you guys. Stay safe.