Robby Robinson said:
I have a job, where we have a 2000 amp feeder from one building to another, we are planning on using 6 sets of 750 mcm aluminum, the feeder is 300 foot long and the computed load on the feeder is 1500 amps. from where we terminate the feeder, we then have a sub feeder to a meter bank, 200 feet away, the feeder will be a 600 amp, using 2 sets of 350mcm copper, the computed load on this feeder is 480 amp. from the meter bank to the furthest condo unit is 150 feet, we are using 3/0 aluminum type mc cable to feed the unit, the computed load on each condo unit is 100 amp.
On the 200 amp feeder, we may use a MC Stabiloy cable, rather then metal conduit.
I was asked by Robby to see if we could get a confirmation on wire sizes we propose to use with the following information. We would like to compare to what we calculated the voltage drop to be, and if we could get some advise as to if the wire sizes that we think we can use would be correct or need to be changed.
1) The feeder from the main tower to the north warehouse building is now 260? long, we want to use 6 sets of 750 mcm al, as the feeder, the voltage is 120/208, 3 phase, the feeder is to be fused at 2000 amp, the calculated load on that feeder is 1500 amp
2) The feeder in the north warehouse distribution area to the meter bank is now 150? it is fused at 600 amp, it is a 120/208 volt, 3 phase feeder with a calculated load of 480 amp, we plan to use two sets of 400 mcm al., as the feeder, of course we could increase the size if necessary.
3) From the meter bank to the furthest condo unit is now 125?, the feeder is a 120/208 volt, single phase feeder, we plan to use 2/0 al. in cable as the feeder, if necessary we could increase the size of this feeder.
4) Now the total distance from the service in the main tower to the last condo unit is 535?.
Any help in this matter would be appreciated.