Oh, but it is. Consider the following...chris kennedy said:Underground and concrete poles so ambient temp is a non-issue.
R2 = R1 [ 1 + α (T2 – 75)], where α = 0.00323 for Cu. See Table 8, Note 2.
T2 = I^2 ? Iampacity^2 ? (75?C – Tambient) + Tambient ***You won't find this one in the NEC***, where Iampacity is 75?C ampacity adjusted for Tambient.
Therefore,
T2 = 10^2 ? (65 x 1.10)^2 ? (75 – 20) + 20 = 21?C, when Tambient is 20?C and assuming a 1.10 ampacity correction factor.
R2 = 0.44 [ 1 + 0.00323 ( 21 – 75)] = 0.36, using effective Z @ 0.85 PF from Table 9
Plugging R2 into your formula,
Vd = 2 ? 0.36 ? 620 ? 10 ? 1000 = 4.46V