e-medic said:When running more amperage on a circuit as allowed using the 90 degree column on NEC table 310.16, the voltage drop formula would require that I run the wire a shorter distance than if I sized using the 75 degree column. Is this correct?
Thanks,
Preston
Dennis Alwon said:Single phase voltage drop:
Vd = 2K x L x I / Cm
For both examples: Vd = voltage drop, K= 12.9 for resistance for a copper conductor
This is true but that fact that you use 90C insulation on the conductor does not change the VD formula. I guess that was the point I was trying to make. The ambient temp. may affect it but not the insulation itself.winnie said:In the above equation, 'K' is the resistance of a copper wire 1 foot long and 1 circular mil in cross section.
This resistance changes with temperature.
For different temperatures, the value of K for copper is:
20C -> 10.1
40C -> 11.5
60C -> 12.9
75C -> 13.9
90C -> 14.9
(For reference, I used the values for copper resistance from http://hyperphysics.phy-astr.gsu.edu/hbase/Tables/rstiv.html#c1 scaled for circular mills and feet rather than meters)
-Jon
Dennis Alwon said:This is true but that fact that you use 90C insulation on the conductor does not change the VD formula. I guess that was the point I was trying to make. The ambient temp. may affect it but not the insulation itself.