Guys,
I have been looking at the voltage drop issue and have a question about the following situations:
To get voltage drop using the IEEE 141 formula and R and I values from Table 9 in the NEC:
Vd=V+IRcos@+IXsin@-sqrt(V^2-(IXcos@-IRsin@)^2)
Looking at large installations (300HP and above), we usually use 2 conductors per phase because it is an easier installation. These parallel conductors will have half the R value, but won't the X (impedance) be double? Can we just use this formula and double the impedance and half the resistance?
Thanks,
Anderman